Metal building roof foam – condensation zone calculations
Working on a 40×80 metal building project in Tennessee (CZ 4A – mixed humid). Owner wants to convert it from agricultural to a climate-controlled shop/garage.
Plan is to spray closed cell foam directly on the metal roof deck and walls. I am concerned about the condensation plane.
With a metal roof, the roof deck gets extremely cold in winter. If I spray 2 inch of closed cell on the interior, is the dew point going to end up within the foam layer, or is 2 inch sufficient to keep the dew point inside the building?
Running the numbers with an online dew point calculator suggests I might need 3-4 inch on the roof to fully control condensation in CZ 4A. Can anyone confirm this from field experience?
Also: what is the typical adhesion like on painted or galvanized metal? Do you prime first?
Join the conversation
You must be logged in to reply to this topic.
CZ4A metal roofs – I use a rule of thumb of R-15 minimum (about 2.5 inch closed cell) for walls and R-25 (about 4 inch) for the roof deck. At 4 inch closed cell, the dew point stays outside the foam layer in CZ4A even on worst-case winter nights. For adhesion on galvanized metal: no primer needed if the metal is clean and dry. On painted metal it depends – fresh acrylic paint is usually fine. Old chalky paint needs light sanding first. Always do a pull test before committing to the full roof.