Doing a crawl space encapsulation job. Customer wants spray foam on the rim joists plus I am doing a full floor system with poly vapor barrier.
Question: If I am spraying 2 inch closed cell on the rim joists, do I still need to extend the poly barrier up the foundation wall to the joists, or does the foam take the place of the vapor control at that location?
Climate zone 5 here (Indiana). IRC 2021 applies.
My understanding: closed cell foam at 2 inch IS a Class II vapor retarder, so the poly is not technically needed at the rim joist location. But I want to make sure there is no air leakage path between the poly on the floor and where the foam starts on the rim.
Also: should I foam the sill plate area before the rim joist, or foam both together?
Join the conversation
You must be logged in to reply to this topic.
Indiana CZ5 contractor here. Yes, 2 inch closed cell on rim joists is a Class II vapor retarder – you do not need poly there. My process: spray the sill plate and 6 inches of foundation wall first, then move up to the full rim joist. This creates a continuous air seal. Then lap the ground poly barrier up the foundation wall 6-8 inches and tape it. Perfect thermal and vapor bridge with no gaps. I have done it this way for 5 years with zero issues.